Alarm template groups
About alarm template groups
Alarm templates can be combined in alarm template groups. With these, users can build alarm template hierarchies allowing alarm thresholds for one or more parameters to be overruled without having to change the base template.
Example of an alarm template group
For this example, we will assume that you apply a template group with three alarm templates (1, 2 and 3) to a protocol with five parameters (A, B, C, D and E).
The following table shows which parameters will be monitored and how. Remember that the order of the alarm templates in a template group is very important as every alarm template in the template group overrules the one below it.
TEMPLATE GROUP Parameter A Parameter B Parameter C Parameter D Parameter E
Template 1 Excluded Excluded Included
Not monitored
Excluded Excluded
Template 2 Included
Not monitored
Excluded Included
Monitored (Threshold 350)
Included
Monitored (Threshold 400)
Excluded
Template 3 Included
Monitored (Threshold 100)
Included
Monitored (Threshold 200)
Included
Monitored (Threshold 300)
Included
Not monitored
Excluded
TEMPLATE GROUP RESULT Included
Not monitored
Included
Included
Not monitored
Included
Excluded
Parameter C, for example, is monitored in both template 2 and template 3 (with different threshold values) but is not monitored in template 1. As a result, parameter C will not be monitored.
If a filtered table parameter is used in one or more alarm templates in the group, each filtered entry in the alarm template is treated as if it were a separate parameter.
Including and excluding parameters in an alarm template
In an alarm template, every parameter can have one of three monitoring states:
Configuration Included in the alarm template Monitored
Included & checkbox selected Yes Yes
Included & checkbox cleared Yes No
Excluded No No
When you edit an alarm template, do not forget to select the Allow include/exclude parameters option in the alarm template settings.
Creating an alarm template group
To create a new alarm template group:
  1. Go to Apps > Protocols & Templates.
  2. Select a protocol in the first column and a protocol version in the second column.
  3. For each alarm template you want to add to the group, do the following:
    1. Right-click the alarm template you want to add and select Open.
    2. Click the cogwheel button at the top of the alarm template editor and make sure the option Allow include/exclude parameters is selected.
    3. In the Included column, check if the correct parameters are included or excluded for alarm template grouping:
      • If the Included column is not displayed, click the settings button and select Allow include/exclude parameters (used for alarm template grouping).
      • For each parameter, a button is displayed that shows Included or Excluded. Click this button to change a parameter from included to excluded or vice versa.
      It is also possible to include or exclude parameters through the template editor right-click menu.
    4. Click OK.
  4. In the Protocols & Templates module, right-click in the third column under Alarm, and select New.
    To create a new alarm template group that is very similar to one that already exists, you can instead duplicate the existing template, by selecting Duplicate in the right-click menu.
  5. In the New alarm template dialog box:
    1. Select Alarm Template Group.
    2. Enter a template group name.
    3. Check if the protocol and protocol version are correct and adapt if necessary.
    4. Click OK.
  6. In the template group editor, click Add Alarm Template and select a template in the drop-down list. Repeat until all the necessary alarm templates are included in the group.
    Under the list with the added alarm templates, the consolidated alarm template is shown. You can use this as a reference to see the combined effect of the different alarm templates in the group.
  7. Hover the mouse pointer over an alarm template and click the small up and down arrows to change the order, if necessary.
    The order of the alarm templates in a template group is very important as every alarm template in the group overrules the one below it.
  8. To remove an alarm template from the group, hover the mouse pointer over the alarm template and click the x.
  9. Click OK.
  • Any alarm templates that are only used in an alarm template group will have the notice Used in group next to the template name in the Protocols & Templates module. If a user tries to delete such an alarm template, he will receive a warning that indicates in which group or groups the template is used.
  • If scheduled alarm templates are used in an alarm template group, they will not be in use in the group at the moment when they are scheduled to be inactive.