Configuring DataMiner processes
Setting the number of simultaneously running SLPort processes
The number of simultaneously running SLPort processes can be set in the <ProcessOptions> tag of the DataMiner.xml file.
The default number is set to 5.
To set a different number:
Stop the DataMiner software.
Open the file
C:\Skyline Dataminer\DataMiner.xml
.Specify a different number for the portProcesses attribute of the ProcessOptions tag.
Example:
<DataMiner> <ProcessOptions portProcesses="2" /> </DataMiner>
Save the file and restart DataMiner.
When elements are spread over the different SLPort processes, the same IP and port are always hosted within the same process. In the log file 'SLPortSplit.txt' you can see which IPs and ports are hosted in the same process.
Setting the number of simultaneously running SLProtocol processes
The number of simultaneously running SLProtocol processes can be set in the <ProcessOptions> tag of the DataMiner.xml file.
The default number of simultaneously running processes depends on the DataMiner version. From DataMiner 10.4.12/10.5.0 onwards, the default number is 10, in earlier DataMiner versions it is 5.
Open the file
.Specify a different number for the protocolProcesses attribute of the ProcessOptions tag.
Example:
<DataMiner> <ProcessOptions protocolProcesses="4" /> </DataMiner>
Adjusting the number of simultaneously running SLProtocol processes will also affect the number of elements that can run in isolation mode. See Adding elements in isolation mode.
Configuring a separate SLProtocol process for every protocol used
For testing purposes, you can order a DataMiner Agent to spread its elements across different SLProtocol processes based on the protocol they are using. If you do so, DataMiner will start up a separate SLProtocol process for every protocol that is used. That way, each SLProtocol process will only contain elements sharing the same protocol. This will make it much easier to pinpoint any protocol-related issues that might arise.
However, note that from DataMiner 10.5.4/10.6.0 onwards, there is a hard limit of maximum 50 SLProtocol processes that can run simultaneously.
As soon as you have concluded the investigation for which you needed this setting to be enabled, disable it again. From DataMiner 10.5.4/10.6.0 onwards, an alarm will be generated when this feature is active to remind you of this.
Warning
Never use this option in a production environment. This feature is meant for testing/debugging purposes only.
To have separate SLProtocol processes created for every protocol being used, do the following.
Open the file
.In the <ProcessOptions> tag, set the protocolProcesses attribute to "protocol".
<DataMiner> <ProcessOptions protocolProcesses="protocol" /> </DataMiner>
Save
.Restart the DataMiner software.
Configuring a separate SLScripting process for every protocol used
If you suspect that a particular protocol is causing a problem in the SLScripting process, then you can have separate SLScripting processes created for every protocol being used. This will then allow you to pinpoint the protocol that is causing the problem.
Warning
To have separate SLScripting processes created for every protocol being used, do the following.
Open the file
.In the <ProcessOptions> tag, set both the protocolProcesses attribute and the scriptingProcesses attribute to "protocol".
<DataMiner> <ProcessOptions protocolProcesses="protocol" scriptingProcesses="protocol" /> </DataMiner>
If scriptingProcesses is set to "protocol", an SLScripting process is initialized for every SLProtocol process (see Configuring a separate SLScripting process for each SLProtocol process). As an SLProtocol process is used for every protocol when protocolProcesses is set to "protocol", combining these two attributes effectively initializes a separate SLScripting process for every protocol.
Save
In a system where the load for one particular protocol has to be spread over several processes, because otherwise too much memory would be needed for one process, it can be useful to have a dedicated SLScripting process created for each SLProtocol process:
Open the file
.In the <ProcessOptions> tag, set the protocolProcesses attribute to a fixed number and the scriptingProcesses attribute to "protocol".
<DataMiner> <ProcessOptions protocolProcesses="18" scriptingProcesses="protocol" /> </DataMiner>
The number you specified determines the number of SLProtocol processes. Elements using the same SLProtocol process will also use the same SLScripting process.
Save
Configuring separate SLProtocol and SLScripting instances for a specific protocol
As some protocols have QActions that require a large amount of memory, elements using these protocols can cause SLScripting to run out of memory when they run together in the same process instance. From DataMiner 10.2.5/10.3.0 onwards, you can prevent this by making such elements run in their own SLProtocol and SLScripting instances.
When a protocol is flagged to run in separate instances, every element using that protocol will be started in a new instance of SLProtocol and SLScripting. When the element is stopped, these instances are taken down again, and when the element restarts, new instances are created.
- From DataMiner 10.2.7/10.3.0 onwards, this behavior can also be configured in the protocol itself using the RunInSeparateInstance tag. In that case, no DataMiner restart is required.
- From DataMiner 10.4.0 [CU13]/10.5.0 [CU1]/10.5.4 onwards, you can configure a specific element to run in its own SLProtocol and SLScripting process using the Run in isolation mode option. This allows you to isolate individual elements without affecting all elements using the same protocol.
To configure this:
Open the file
.In the <ProcessOptions> element, specify a <SeparateProcesses> element listing the protocols that should run in separate SLProtocol and SLScripting instances. For example:
<DataMiner> ... <ProcessOptions protocolProcesses="3" scriptingProcesses="protocol"> <SeparateProcesses> <Protocols> <Protocol> <Name>MyElementProtocol</Name> </Protocol> </Protocols> </SeparateProcesses> </ProcessOptions> ... </DataMiner>
Save
- A separate SLScripting process must be launched for every SLProtocol process. This means that when at least one protocol name is specified in the SeparateProcesses tag, the configuration of the scriptingProcesses attribute will be overridden to "protocol", except if it is set to "[Service]" (see Running SLScripting as a service). Configuring separate SLProtocol and SLScripting instances for a protocol is not compatible with a configuration where SLScripting is configured as a service. If you do configure both of these options, the configuration to run separate SLProtocol and SLScripting instances will be ignored, and a notice alarm will be generated with more information.
- DataMiner.xml files are not synchronized in a DMS. If your DMS consists of multiple DMAs, you will need to edit the DataMiner.xml file on each of the DMAs.
Having replicated elements handled by one SLProtocol process
In order to reduce the number of connections in case of element replication, in the DataMiner.xml file, you can specify that all replicated elements from the same remote DataMiner Agent have to be handled by the same SLProtocol process.
To do so:
Open the file
.Set the protocolProcesses attribute of the <ProcessOptions> tag to "replicationIP":
<DataMiner>
<ProcessOptions protocolProcesses="replicationIP"/>
</DataMiner>
Setting the number of simultaneously running SLScripting processes
From DataMiner 10.2.7/10.3.0 onwards, the number of simultaneously running SLScripting processes can be set in the <ProcessOptions> tag of the DataMiner.xml file.
Open the file
.In the <ProcessOptions> tag, set the scriptingProcesses attribute to the desired number. For example:
<DataMiner> <ProcessOptions protocolProcesses="5" scriptingProcesses="3" /> </DataMiner>
Save
The SLProtocol processes will be assigned one of the available SLScripting processes in a round-robin way. For example, if protocolProcesses is set to 5 (i.e. the default value), and scriptingProcesses is set to 3:
- SLScripting 1 will host SLProtocol #1 and #4
- SLScripting 2 will host SLProtocol #2 and #5
- SLScripting 3 will host SLProtocol #3
Assigning more SLScripting processes than SLProtocol processes will give every SLProtocol process its own instance without launching additional SLScripting processes.
This configuration is no longer supported. See Software support life cycles.
By default, the SLScripting process runs as a server. However, in some cases, it needs to run as a service. It is possible to configure this in the file DataMiner.xml:
To register SLScripting as a service
Open the file
.Make sure DataMiner.xml contains a <ProcessOptions> tag and that it contains the scriptingProcesses="[Service]" attribute:
<ProcessOptions ... scriptingProcesses="[Service]" .../>
Open a command window as Administrator, and do the following:
Go to
C:\Skyline DataMiner\Files
.Execute the following command: SLScripting.exe /service
Start the DataMiner software.
To register SLScripting as a server
Open the file
.If DataMiner.xml contains a <ProcessOptions> tag with a scriptingProcesses="[Service]" attribute, remove that attribute:
Go to
.Execute the following command: SLScripting.exe /regserver
SLWatchdog
On a DataMiner Agent, the SLWatchdog process continuously monitors all other DataMiner processes. When it detects some kind of problem with one of those processes, it takes action.
Caution
SLWatchdog must never be started or restarted manually when DataMiner is running. Doing so may have unintended consequences as it guards the DataMiner processes.
When will SLWatchdog take action?
In Windows Task Manager, the DataMiner processes all have names starting with "SL". SLWatchdog will take action in either of the following cases:
When a DataMiner process has disappeared from the list of running processes.
When an anomaly has been detected in a DataMiner process.
In this case, SLWatchdog will do the following:
Send an email message stating the name of the DataMiner process toward all recipients specified in the SLWatchdog configuration settings. By default, this message will include a dump file containing copies of all DataMiner log files found on the DataMiner Agent the moment the problem was detected.
Restart the process (in case the process that disappeared was SLScripting), or restart the DataMiner Agent as a whole (in case the process that disappeared was not SLScripting, but one of the other processes, which in many cases have a number of dependencies).
Create two information messages:
One at the moment the DataMiner Agent is stopped.
One at the moment the DataMiner Agent is restarted.
Both messages will be displayed in the DataMiner Alarm Console.
Create an alarm with severity "Error", which will be displayed in the DataMiner Alarm Console. This alarm will contain detailed information about the anomaly.
Optionally restart the DataMiner Agent. By default, this will not be done.
Configuring the SLWatchdog process
In the file MaintenanceSettings.xml, you can specify a number of SLWatchdog settings.
Open the file
C:\Skyline DataMiner\MaintenanceSettings.xml
.In the Watchdog tag, modify the SLWatchdog settings (see below).
Save
.Stop the DataMiner Agent.
Manually stop the SLWatchdog service.
Restart the DataMiner Agent.
See also: MaintenanceSettings.xml
Example of an SLWatchdog tag in MaintenanceSettings.xml
<MaintenanceSettings>
<WatchDog>
<TimeoutTime>5</TimeoutTime>
<Errors>2</Errors>
<Actions>Alarm</Actions>
<EMail active="true">
<Destination></Destination>
<CCDestination></CCDestination>
<BCCDestination></BCCDestination>
</EMail>
<ProcessMonitor maxinHour="3"
maxProcess="2"
maxTimeout="2"
maxAttachmentSize="5"
passwordOnAttachment="true" />
</WatchDog>
</MaintenanceSettings>
Overview of the different SLWatchdog settings
The following table contains all information about the different SLWatchdog settings you can configure in the Watchdog tag of MaintenanceSettings.xml.
Tag | Attribute | Description |
TimeoutTime | - | The interval (in minutes) between two consecutive process thread checks. Default value: 5 |
Errors | - | The number of process thread checks that are allowed to return an error before SLWatchdog will consider the situation to be an anomaly. Default value: 2 |
Actions | - | List of actions (separated by semicolons) to be performed upon detection of an anomaly. Possible values are "Alarm" and "Restart". Default value: "Alarm" |
active | If true, SLWatchdog will send email messages upon detection of an anomaly. Default value: true | |
Email.Destination | - | The "To" recipients, separated by semicolons. Default value: dataminer.minidump@skyline.be |
Email.CCDestination | - | The "CC" recipients, separated by semicolons. By default, this tag is empty. |
Email.BCCDestination | - | The "BCC" recipients, separated by semicolons. By default, this tag is empty. |
ProcessMonitor | maxInHour | SLWatchdog will perform the specified actions if the situation does not occur more than X times in one hour. Default value: 3 |
ProcessMonitor | maxProcess | SLWatchdog will perform the specified actions if a maximum of X processes have disappeared within the time span defined in maxTimeout. Default value: 2 |
ProcessMonitor | maxTimeout | SLWatchdog will perform the specified actions if more processes than defined in maxProcess have disappeared within a time span of X minutes. Default value: 2 |
ProcessMonitor | maxAttachmentSize | The maximum size (in MByte) of the dump file that will be attached to the email messages. If exceeded, a so-called mini dump file will be attached. Default value: 5 |
ProcessMonitor | passwordOnAttachment | If true, users will have to enter the password "Skyline" in order to access the dump files attached to the email messages. Default value: false |
Configuring SLNet settings in MaintenanceSettings.xml
Before you configure any of these settings, you will need to stop DataMiner. After you have saved your changes, restart DataMiner again.
Limiting the number of connection attempts
Using the following tags, you can limit the number of connection attempts per client computer that a DataMiner Agent will allow.
MaxConnectionAttemptsCheckEnabled (default: true)
MaxConnectionAttempts (default: 40)
MaxConnectionAttemptsTime (default: 2 minutes)
These settings do not apply to replication connections.
Example:
<SLNet>
<MaxConnectionAttemptsCheckEnabled>true</MaxConnectionAttemptsCheckEnabled>
<MaxConnectionAttempts>40</MaxConnectionAttempts>
<MaxConnectionAttemptsTime>2</MaxConnectionAttemptsTime>
</SLNet>
If you specify the above-mentioned connection attempt settings, a DataMiner Agent will disregard all subsequent attempts and return the following error message when it receives more than 40 connection attempts within 2 minutes:
Too many connection attempts from client XXXXX.
Enabling encrypted connections
If you set the RequireEncryptedConnections tag to TRUE, then all incoming connections have to use encryption.
When a legacy DMA tries to connect to a DMA that requires encrypted connections, the following message will be returned:
Client software does not support encrypted connections.
Example:
<SLNet>
<RequireEncryptedConnections>TRUE</RequireEncryptedConnections>
</SLNet>
Default from DataMiner 10.1.7 onwards: TRUE
Configuring the number of messages to be returned (polling/eventing)
Using the following tags, you can specify the number of messages to be returned in case of polling or eventing:
MaxMessagesPerPollingRequest: The maximum number of events to be returned after a polling request. Default: 500 events
MaxMessagesPerCallback: The maximum number of events to be sent via an eventing callback. Default: 500 events
Polling requests are usually sent less often than eventing callbacks. Normally, callbacks are sent every 100 ms, while polling requests are sent every second (depending on the configuration).
Example:
<SLNet>
<MaxMessagesPerPollingRequest>2000</MaxMessagesPerPollingRequest>
<MaxMessagesPerCallback>500</MaxMessagesPerCallback>
</SLNet>
- When a single polling response is not able to empty the stack of queued messages on the server, the next polling request will be scheduled after 100ms (fixed value).
- Unzipping/unpacking polling response data on the client can be done while another polling request is already in progress.
Configuring the polling request timeout
In the <DefaultPollingRequestTimeout> tag, you can set the polling request timeout (in seconds).
This setting will apply to all new inter-DMA connections set up from that DMA.
Default value: 60 seconds
See also: Configuring the polling request timeout
Configuring indexing options for the server-side search of DataMiner Cube
In the <SearchOptions> tag, you can configure the indexing options for the server-side search of DataMiner Cube.
Example:
<SLNet>
<SearchOptions>trendedParamsOnly</SearchOptions>
</SLNet>
See also: Setting the indexing options for the server-side search
Making DataMiner Cube ignore view updates
If you set the <ClientSkipViewUpdates> tag to TRUE, DataMiner Cube clients will no longer handle any view changes.
The first time a view change has been ignored, a Reconnect button will appear at the top of the Surveyor. Click this button to reconnect and manually reload any view changes.
Example:
<SLNet>
<ClientSkipViewUpdates>TRUE</ClientSkipViewUpdates>
</SLNet>
Default: FALSE
This setting can also be configured with the SLNetClientTest tool. However, note that this is an advanced administration tool that should be used with extreme care. See Making DataMiner Cube ignore view updates.
Specifying DCF settings
Within the <SLNet> tag, several settings for the DCF engine can be configured.
ConnectivityEngineInterval
Use this setting to specify (in milliseconds) how frequently the DCF engine has to check for changes in connectivity chains. By default, the interval is set to 1000 milliseconds.
Example:
<SLNet>
<ConnectivityEngineInterval>5000</ConnectivityEngineInterval>
</SLNet>
ConnectivityLogVerbose
Set this setting to "true" to add extra information in the logs with regard to connectivity chain resolution.
Example:
<SLNet>
<ConnectivityLogVerbose>true</ConnectivityLogVerbose>
</SLNet>
ConnectivityMaxConnections
Use this setting to specify the maximum number of connections that is allowed in Connectivity event and response messages. By default, the maximum number of connections is set to 500.
Example:
<SLNet>
<ConnectivityMaxConnections>700</ConnectivityMaxConnections>
</SLNet>
Activating the NonElementProtocol option system-wide
In a Visual Overview, a "NonElementProtocol" option can be specified in case it contains shapes linked to a large number of elements, but no element-specific formatting is needed from files like description.xml, informations.xml, or port.xml. This can enhance the overall performance of the Visual Overview.
It is also possible to apply this option system-wide, instead of limiting it to one Visual Overview shape or page.
To do so, add a <NonElementProtocol> tag in the <SLNet> section of the MaintenanceSettings.xml file, and set this tag to "true".
Example:
<SLNet>
<NonElementProtocol>true</NonElementProtocol>
</SLNet>
See also: NonElementProtocol
Generating information events when a connection fails to authenticate
It is possible to have an information event generated whenever a connection fails to be authenticated. From DataMiner 10.1.8/10.2.0 onwards, this is enabled by default.
To enable this option in older systems, add an <EnableFailedAuthenticationInfoEvents> tag in the <SLNet> section of the MaintenanceSettings.xml file, and set this tag to "true".
Example:
<SLNet>
<EnableFailedAuthenticationInfoEvents>true</EnableFailedAuthenticationInfoEvents>
</SLNet>
Configuring a cluster transition state timeout
In the <ClusterTransitionStateTimeout> tag, you can specify a cluster transition state timeout (in seconds).
DataMiner Agents leaving the DataMiner System (i.e. cluster) will leave the transition state after the specified timeout delay, starting from the last received notification from any of the DataMiner processes.
Example:
<SLNet>
<ClusterTransitionStateTimeout>5</ClusterTransitionStateTimeout>
</SLNet>
Fine-tuning NATS settings
From DataMiner 10.1.0/10.1.1 onwards, DataMiner processes use the NATS open-source messaging system to communicate with each other. Some settings for NATS can be fine-tuned in MaintenanceSettings.xml, using the following tags:
NATSDisasterCheck: Set this to true or false in order to respectively activate or deactivate automatic detection and triggering of NATS cluster self-healing (default: false).
NATSResetWindow: Specify a value in seconds to set a window during which only one NATS reset can occur. This prevents situations where NATS disaster recovery is triggered too often. The minimum value is 60. If a lower value is specified, 60 will be used instead.
NATSLogFileCleanupMs: Supported from DataMiner 10.1.0 [CU9]/10.1.8 onwards. Determines the time (in milliseconds) between NATS log file cleanup attempts. This timing will only be applied after the next cleanup attempt after the configuration change. For example, if the next cleanup attempt is in 15 minutes, and you change this value, the next cleanup will still be in 15 minutes, but all subsequent cleanups will happen after 1-minute intervals. The default value of this setting is 900000 (15 minutes).
NATSLogFileAmountToKeep: Supported from DataMiner 10.1.0 [CU9]/10.1.8 onwards. The number of log files to keep (default =10). This value only applies to the log files that do not have the .log extension.
Example:
<SLNet>
<NATSDisasterCheck>true</NATSDisasterCheck>
<NATSResetWindow>90</NATSResetWindow>
<NATSLogFileCleanupMs>60000</NATSLogFileCleanupMs>
<NATSLogFileAmountToKeep>20</NATSLogFileAmountToKeep>
</SLNet>
From DataMiner 10.1.0/10.1.3 onwards, you can instead configure this using the SLNetClientTest tool. See Fine-tuning NATS settings.
Fine-tuning message throttling
From DataMiner 10.2.0/10.1.2 onwards, message throttling is enabled on connections from web applications (e.g. Monitoring app, Dashboards app, Web APIs, etc.) to SLNet. This is a mechanism that avoids an excessive number of parameter update messages being sent at the same time.
From DataMiner 10.1.3 onwards, the following settings can be fine-tuned for this in MaintenanceSettings.xml:
MessageThrottlingThreshold: Time interval in ms. The default and minimum value is 250. If two updates for the same parameter are received within this interval, message throttling is activated. The first of the parameter updates is sent immediately, but messages for the same parameter that come after this are throttled until no more parameter updates have been received for this same time interval. Once the throttling has stopped, the last update is also sent after at most this time interval.
MessageThrottlingPeriodicUpdate: Time interval in ms. The default value is 1000, and the value must always be at least twice the MessageThrottlingThreshold value. If there is a steady flow of updates for the same parameter, and message throttling is activated, a periodic update is sent after this interval.
Example:
<SLNet>
<MessageThrottlingThreshold>250</MessageThrottlingThreshold>
<MessageThrottlingPeriodicUpdate>1000</MessageThrottlingPeriodicUpdate>
</SLNet>
Customizing how long a connection ticket remains valid
When establishing a new connection (e.g. using the DataMiner Web Services), SLNet makes use of a ticket for authentication. The AuthenticationTicketExpirationTime setting in MaintenanceSettings.xml determines how long this ticket remains valid. If a request for a new connection is made after the specified time has elapsed, the system will consider the request invalid.
By default, this is set to 30 seconds.
Example:
<SLNet>
<AuthenticationTicketExpirationTime>30</AuthenticationTicketExpirationTime>
</SLNet>
Within the SLNet element in MaintenanceSettings.xml, there is also a TicketExpirationTime setting. This determines the duration (in seconds) that a ticket used to perform privileged instructions remains valid (default value: 300 seconds). This is for instance used to grant a user permission to start DataMiner. If a request for the privileged instruction is made after the specified time period has passed, the system considers the ticket invalid and denies the request.
Disabling .NET Remoting
By default, .NET Remoting is used for communication between DMAs. From DataMiner 10.3.2/10.3.0 onwards, a gRPC connection can be used instead. To make gRPC the default for communication between DMAs, you can either add Redirect tags in DMS.xml, or disable .NET Remoting in MaintenanceSettings.xml. However, note that the latter is only recommended from DataMiner 10.3.6/10.3.0 [CU3] onwards, as prior to this there is no support for DataMiner upgrades over gRPC.
To do the latter, add an <EnableDotNetRemoting> tag in the <SLNet> section of the MaintenanceSettings.xml file, and set this tag to "false".
Example:
<SLNet>
<EnableDotNetRemoting>false</EnableDotNetRemoting>
</SLNet>
Make sure this is configured the same way for all Agents in a DMS.
Configuring a 'keep alive' interval for the connection
In DataMiner Systems with unstable network connectivity, gRPC calls between SLNet instances can take a long time. From DataMiner 10.4.0 [CU10]/10.5.1 onwards, this is limited to at most 15 minutes. From these DataMiner versions onwards, you can also configure the HttpTcpKeepAliveInterval option to prevent issues on Agents that are known to have such connectivity problems.
With this option, after the configured number of seconds of inactivity (60 in the example below), DataMiner will check if the connection is still active by sending a "keep-alive" packet. As long as there is no response, every 5 seconds a new keep-alive packet is sent. If there is still no response after 10 packets have been sent, the connection will be closed.
Example:
<SLNet>
<HttpTcpKeepAliveInterval>60</HttpTcpKeepAliveInterval>
</SLNet>
Caution
Do not use this feature in networks where a firewall drops TCP keep-alive packets. Using it in such a network could cause the connection to be closed while it is actually still working.
Configuring the maximum upload size for upgrade packages
The maximum upload size for upgrade packages is determined by the MaxUploadSize
setting in MaintenanceSettings.xml.
To change this, you can use the SLNetClientTest tool (see Increasing the maximum upload size for upgrade packages in a DMS), or you can directly modify MaintenanceSettings.xml. However, note that the latter requires a DataMiner restart.
The default maximum upload size of upgrade packages is 4000 MB.
Example:
<SLNet>
<MaxUploadSize>1300</MaxUploadSize>
</SLNet>
Enabling information events when scripts are started by Correlation rules or scheduled tasks
From DataMiner 10.5.2/10.6.0 onwards, by default no information events are generated when Automation scripts are triggered by the Correlation engine. From DataMiner 10.5.4/10.6.0 onwards, this also applies to Automation scripts triggered by the Scheduler module.
If you do want information events to be generated when scripts are triggered by Correlation rules or scheduled tasks, add the SkipInformationEvents
option to the MaintenanceSettings.xml file and set it to "false":
<MaintenanceSettings xmlns="http://www.skyline.be/config/maintenancesettings">
<SLNet>
<SkipInformationEvents>false</SkipInformationEvents>
</SLNet>
Configuring the port for .NET Remoting
On a DMA, you can specify the port to be used for .NET Remoting.
Go to the
directory of the DMA.In a text editor (e.g. Microsoft Notepad), open SLNet.exe.config.
In the Channels section, go to the channel tag named SLNetRemoting, and set its "port" attribute to the port number to be used for .NET Remoting. By default, this will be port 8004:
<channel ref="http" name="SLNetRemoting" port="8004" timeout="300000" clientConnectionLimit="200">
See also: Overview of IP ports used in a DMS
Save and close the file.
Restart DataMiner.